​ ​ ​ ​ Possible Picaxe Software Problem?
Page 1 of 3 1 2 3 LastLast
Results 1 to 10 of 21

Thread: Possible Picaxe Software Problem?

  1. #1
    Member
    Join Date
    Sep 2007
    Location
    Canberra, Australia
    Posts
    90

    Default Possible Picaxe Software Problem?

    I have an 08M2 picaxe that is acting quite strangely and I’m starting to think it’s a problem with the picaxe and not me. I know the odds are against me but ...

    The attached is a slight variant of a program that I’m currently using to monitor a water meter fitted with a reed switch that opens after every ½ a litre of flow. The version currently operating suffers from the occasional random reset every few days (which I can live with) but the attached one should reset within 8 minutes. The difference between the two versions is line 181 (nap 2) has been commented out and the HC-12 sleep test in the SleepMod subroutine has been altered so that the program can run on an 08M2 that isn’t connected to an HC-12 transceiver - so you can check it out.

    The program simple transmits some numbers (incremental pulse counter and battery voltages) every time the reed switch in the meter opens. It also periodically checks that the 2 * 25 mA solar panels aren’t overcharging the battery and if the battery voltage is high, it doesn’t put the HC-12 to sleep.

    The program worked fine while I was simulating water meter reed switch pulses for high flow rates through the meter using a relay and another 08m2 but when I was checking for periods of no water use, the program kept continually resetting while the relay was open but not when it was closed. And the resetting was occurring at regular precise times (about every 14 minutes). I initially suspected it was something to do with my periodic battery overvoltage checking although I wondered how that could ever get the program to reset.

    Anyway, I played around with a number of things trying to isolate the problem and changed a few things and added sertxd statements at various points in the program. Making these changes sometimes made the problem disappear and other times changed the resetting period. For example, changing the nap period in the section of code where its looping around step 9, from “nap 3” to “nap 2” halved the reset period down to a regular 7 minutes while changing it to “nap 1” made a problem disappear as did substituting 2 lots of “nap 2” (which is the version I’m currently using). Also adding a sertxd as it entered the bit of code that checks for battery over-voltage in step 9 stopped the resets.

    I don’t think its hardware related as I’ve tried it on a couple of 08M2’s with different power supplies and the behaviour is the same. I had a similar problem way back in early 2007 soon after I first used an 08m2. Then it involved the use of the sleep command which caused the 08m2 to restart at fixed intervals – just like this present case. I wrote to the forum about it and you fixed it. I can’t refer to that thread as they don’t go back that far. I just wondered if the” nap” command had anything to do with it. Certainly, changing it to “pause” appeared to stop the restarts but as I say, other program changes that I would have thought should have no effect on the restarts also stopped it. I’d prefer to use “nap” in order to minimize power use as in winter, solar input could be quite low.

    I’m using PE5 (version 5.5.5) as I’ve not got around to upgrading to PE6. I realize that you regard PE5 as obsolete but hopefully you’ll still consider this problem.

    Actually, it looks like I can't include the code here as it make the submission too big so I'll send it in the next post.

  2. #2
    Member
    Join Date
    Sep 2007
    Location
    Canberra, Australia
    Posts
    90

    Default

    Here is a version of the program that dosn't need an HC-12 to be attached that you can test to see if you get the same result as I got.

    Code:
    #rem
    This version includes a check for high battery voltages which are periodically done in steps 2 & 9.
    
    This program initially displays (@19200 baud) its set-up mode
    Start
    BPTR=61
    OK+B9600
    OK+RC001
    OK+RP:+20dBm
    
    1.	Initialize
    2.	Raise pullup on c.4; Readadc C.4 and reset c.4 pullup
    3.	If adc reading is low then nap 2 for 72 msecs and goto 2.
    4.	Nap 1 for 32 msecs and then readadc again to confirm that its high. If low, goto 2
    5.	Wake up HC-12
    6.	Increment water pulse counter (WPC) and calculate battery voltage (BV)
    7.	Transmit #WPC, #Battery voltages and #WPC again for redundancy (but later use without # when received by 08M2)
    8.	Put HC-12 to sleep
    9.	Check reed switch (as per 2.). If closed, goto 2 else nap 3 for 144 msecs and goto 9. 
    
    The module draws about 0.7 mA when the battery voltage is about 4 volts and the HC-12 is asleep.
    
    If the HC-12 can't be put to sleep after 5 attempts, the program simply transmits "Can't sleep HC-12" every 67 secs and naps between times.
    
    #endrem
    
    #picaxe 08M2
    #no_data
    
    symbol rx = c.3		'connected to Txd on module
    symbol tx = c.2		'connected to Rxd on module
    symbol con = c.1	'connected to Con on module
    symbol GreenLED=c.0	'connected to green LED and also used here as an earth return for the reed switch
    
    'bytes b0-b2 used
    symbol suppmin=b3
    symbol WaterCnt=w2
    symbol suppvol=w3
    symbol suppmax=b8
    symbol temp=b9
    symbol BatVoltInt=w5	'counter to trigger a battery over-voltage check
    symbol BatOvrVolt=b12	'=0 if less than 215 (ie 4.15 volts)
    
    symbol BattHigh=215
    symbol BattLow=210
    
    
    'check the HC-12 parameters
    
    high Tx
    low con	'put into command mode (to communicate at previouslt set baud rate)
    pause 40	'wait for module to go into command mode
    
    setfreq M16	'seems to need 16MHz to operate at 9600
    
    sertxd ("Start",cr,lf)
    
    serout tx,T9600_16,("AT+RX")  
    
    bptr=28
    serin [1000],rx,T9600_16,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc
    
    b0=bptr-1
    bptr=28
    sertxd ("BPTR=",#b0,cr,lf)
    for b1=bptr to b0
    	sertxd (@bptrinc)
    next b1
    
    input con	'take out of command mode and tri-state c.1
    pause 160	'wait 40 msecs for module to go into pass through mode
    
    BatOvrVolt=0	'set over voltage flag off
    gosub sleepmod	'put HC-12 to sleep to save power
    
    '-----------------------------------------------------------------------------------
    
    stp1:
    low GreenLED	'used as earth return for reed switch in water meter
    suppmin=255
    symbol reedmin=50
    
    stp2:
    BatVoltInt=BatVoltInt+1 and $0FFF	'should overflow about every 5 minutes
    if BatVoltInt=0 then
    	calibadc10 suppvol
    	suppvol=64*1023/suppvol*200/125	'Supply Voltage
    	suppvol=suppvol-200
    	if suppvol>BattHigh then
    		if BatOvrVolt=0 then
    			BatOvrVolt=1
    			low con		'put into command mode (to communicate at previouslt set baud rate)
    			pause 160	'wait 40 msecs for module to go into command mode
    			input con	'take out of command mode and tri-state c.1
    			pause 160	'wait 40 msecs for module to go into pass through mode
    		endif
    	endif
    	if suppvol<BattLow then
    		if BatOvrVolt>0 then
    			BatOvrVolt=0
    			call sleepmod
    		endif
    	endif
    else
    	nap 2	'nap for 72 msecs
    endif		
    	
    pullup %00010000
    readadc c.4,b0
    pullup %00000000
    'sertxd (#b0,cr,lf)
    if b0<reedmin then : goto stp2: endif	'nap for 72 msecs if contacts closed
    
    stp4:
    nap 1	'nap for 32 msecs
    pullup %00010000
    readadc c.4,b0
    pullup %00000000
    if b0<reedmin then stp2	'pulse needs to be high for at least 32 msecs
    
    stp5:
    high c.0	'green led on
    high Tx
    low con		'put into command mode (to communicate at previouslt set baud rate)
    pause 160	'wait 40 msecs for module to go into command mode
    'nap 2	'nap for 72 msecs
    input con	'take out of command mode and tri-state c.1
    pause 160	'wait 40 msecs for module to go into pass through mode
    'nap 2	'nap for 72 msecs
    low c.0	'green led off
    
    stp6:
    inc WaterCnt	'increment the water meter pulse counter
    
    calibadc10 suppvol
    suppvol=64*1023/suppvol*200/125	'Supply Voltage
    suppvol=suppvol-200
    suppmax=suppvol min suppmax
    suppmin=suppvol max suppmin
    '	sertxd (#Suppvol,",",#suppmax,",",#suppmin,cr,lf)
    
    
    stp7:
    serout tx,T9600_16,(#WaterCnt," - ",#suppvol,",",#suppmax,",",#suppmin,",",#WaterCnt,cr,lf)
    'input tx		'tri-state tx pin c.2
    pause 150	'it just seems to need a pause here of at least 50 for it to work
    
    stp8:
    if BatOvrVolt=0 then: gosub sleepmod:endif	'put HC-12 to sleep to save power if battery not overcharged
    
    stp9:
    pullup %00010000
    readadc c.4,b0
    pullup %00000000
    if b0<reedmin then
    	goto stp2
    else
    	BatVoltInt=BatVoltInt+1 and $0FFF	'should overflow about every 5 minutes
    	if BatVoltInt=0 then
    'sertxd ("Stp 9 - BatVoltInt=0",cr,lf)
    		calibadc10 suppvol
    		suppvol=64*1023/suppvol*200/125	'Supply Voltage
    		suppvol=suppvol-200
    		if suppvol>BattHigh then
    			if BatOvrVolt=0 then
    				BatOvrVolt=1
    				low con		'put into command mode (to communicate at previouslt set baud rate)
    				pause 160	'wait 40 msecs for module to go into command mode
    				input con	'take out of command mode and tri-state c.1
    				pause 160	'wait 40 msecs for module to go into pass through mode
    			endif
    		endif
    		if suppvol<BattLow then
    			if BatOvrVolt>0 then
    				BatOvrVolt=0
    				call sleepmod
    			endif
    		endif
    	else
    		nap 2		'nap for 144 msecs if contacts still open
    '		nap 2		'nap for 144 msecs if contacts still open
    	endif		
    	
    	goto stp9	'loop here indefinitely until contacts close again
    endif
    
    
    '-----------------------------------------------------------------------------------
    sleepmod:	'Puts module to sleep - takes about 150 msecs and leaves it in pass through mode
    temp=5
    rpt:high Tx
    low con	'put into command mode (to communicate at previouslt set baud rate)
    pause 160	'wait 40 msecs for module to go into command mode
    'sertxd ("Go to sleep",cr,lf)
    
    serout tx,T9600_16,("AT+SLEEP")  
    
    bptr=28
    serin [150],rx,T9600_16,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc
    
    b0=bptr-1
    pause 160	'wait 40 msecs to action sleep command before going back to pass through mode
    input con	'take out of command mode by tri-stating c.1
    
    #rem
    bptr=28
    sertxd ("BPTR=",#b0,cr,lf)
    for b1=bptr to b0
    	sertxd (@bptrinc)
    next b1
    #endrem
    
    'if b0<>37 then
    if b0=0 then
    	low con		'put into command mode (to communicate at previouslt set baud rate)
    	pause 160	'wait 40 msecs for module to go into command mode
    	'nap 2	'nap for 72 msecs
    	input con	'take out of command mode and tri-state c.1
    	pause 160	'wait 40 msecs for module to go into pass through mode
    	'nap 2	'nap for 72 msecs
    	serout tx,T9600_16,("Can't sleep ",#b0,cr,lf)
    	sertxd ("Can't sleep ",#b0,cr,lf)
    	pause 150	'it just seems to need a pause here of at least 50 for it to work
    	if temp>0 then
    		dec temp
    		goto rpt	'repeat straight away if haven't tried 5 times already
    	else
    		nap 12	'nap for 67 secs
    		goto rpt	'repeat after 67 secs if have tried 5 times already
    	endif
    endif
    
    input tx  	'tri-state c.2 while asleep
    
    return
    '-----------------------------------------------------------------------------------

  3. #3
    Senior Member
    Join Date
    Feb 2010
    Location
    Don't Mess With My Texas!
    Posts
    2,330
    Blog Entries
    5

    Default

    Bill, be careful with these serout vs. serin commands for the HC-12.

    Code:
    serout tx,T9600_16,("AT+SLEEP")  
    
    bptr=28
    serin [150],rx,T9600_16,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc
    You are sending out "AT+SLEEP", the HC-12 is returning "OK+SLEEP" (8 characters), but your serin (without a timeout parameter) is waiting for "@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bpt rinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc" (10 characters.)
    - Tex
    __________________________________________________ _______________________
    These words are my opinion, WYLION. Any resemblance to truth or fiction is accidental at best.
    "Truth lies dormant in our future history." ― Tex Clodhopper LXVI
    "Confidence is ignorance. If you're feeling cocky, it's because there's something you don't know." ― Eoin Colfer, Artemis Fowl

  4. #4
    Technical Support
    Join Date
    Jan 1970
    Location
    UK
    Posts
    24,033

    Default

    Code:
    bptr=28
    serin [150],rx,T9600_16,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc
    b0=bptr-1
    if b0=0 then
    I can't see how that's condition is ever going to evaluate true.

  5. #5
    Senior Member
    Join Date
    Feb 2009
    Location
    Cheshire, England
    Posts
    2,426
    Blog Entries
    4

    Default

    Quote Originally Posted by hippy View Post
    ... I can't see how that's condition is ever going to evaluate true.
    What he needs is a BBW ( Branch Both Ways ) instruction

    I thought BBW was a joke, until I learnt a bit more about the Spectre and Meltdown exploits.
    These use info gained when your CPU executes both paths of a yes/no descision simultaneously.

    Modern tech - too clever by half !

  6. #6
    Member
    Join Date
    Sep 2007
    Location
    Canberra, Australia
    Posts
    90

    Default

    Quote Originally Posted by hippy View Post

    I can't see how that's condition is ever going to evaluate true.
    That's the point, it can't be true for the version of the program I posted. The real statement is the adjacent one that is commented out. I only changed the statement so that the version that I hope you'll try out won't get caught up in the "Can't sleep" portion of the program because you won't have an HC-12 connected to the 08M2.

  7. #7
    Senior Member
    Join Date
    Sep 2011
    Location
    Montpellier (FRANCE)
    Posts
    2,714

    Default

    goto stp9
    will continue to
    Sleepmod :

    same problem with :
    goto rpt

    But Sleepmod end with a RETURN, called where ?

    Answer this question and maybe you can understand why some behaviour where "strange" ...
    IMHO, one GOTO within that kind of program is one GOTO in excess...
    Last edited by BESQUEUT; 12-02-2018 at 17:21.
    There are 10 types of people in the world: those who understand binary, and those who don't.

  8. #8
    Technical Support
    Join Date
    Jan 1970
    Location
    UK
    Posts
    24,033

    Default

    Quote Originally Posted by BESQUEUT View Post
    goto stp9
    will continue to
    Sleepmod :
    I don't think so; there are GOTO commands which are tucked inside the IF-ELSE-ENDIF blocks which will prevent that. But those and other GOTO commands do make the program flow rather difficult to follow.

    As PE5 is being used I would suggest trying PE6 to see if that does change things.

  9. #9
    Senior Member
    Join Date
    Sep 2011
    Location
    Montpellier (FRANCE)
    Posts
    2,714

    Default

    Quote Originally Posted by hippy View Post
    I don't think so; there are GOTO commands which are tucked inside the IF-ELSE-ENDIF blocks which will prevent that. But those and other GOTO commands do make the program flow rather difficult to follow.

    As PE5 is being used I would suggest trying PE6 to see if that does change things.
    You are true, and as of #4, no problem with the goto rpt...

    Not sure that this program is strictly equivalent, but easier to read :
    Code:
    #picaxe 08M2
    #no_data
    
    symbol rx = c.3		'connected to Txd on module
    symbol tx = c.2		'connected to Rxd on module
    symbol con = c.1	'connected to Con on module
    symbol GreenLED=c.0	'connected to green LED and also used here as an earth return for the reed switch
    
    'bytes b0-b2 used
    symbol suppmin=b3
    symbol WaterCnt=w2
    symbol suppvol=w3
    symbol suppmax=b8
    symbol temp=b9
    symbol BatVoltInt=w5	'counter to trigger a battery over-voltage check
    symbol BatOvrVolt=b12	'=0 if less than 215 (ie 4.15 volts)
    
    symbol BattHigh=215
    symbol BattLow=210
    
    
    'check the HC-12 parameters
    
    high Tx
    low con	'put into command mode (to communicate at previouslt set baud rate)
    pause 40	'wait for module to go into command mode
    
    setfreq M16	'seems to need 16MHz to operate at 9600
    
    sertxd ("Start",cr,lf)
    
    serout tx,T9600_16,("AT+RX")  
    
    bptr=28
    serin [1000],rx,T9600_16,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc
    
    b0=bptr-1
    bptr=28
    sertxd ("BPTR=",#b0,cr,lf)
    for b1=bptr to b0
    	sertxd (@bptrinc)
    next b1
    
    input con	'take out of command mode and tri-state c.1
    pause 160	'wait 40 msecs for module to go into pass through mode
    
    BatOvrVolt=0	'set over voltage flag off
    gosub sleepmod	'put HC-12 to sleep to save power
    
    
    low GreenLED	'used as earth return for reed switch in water meter
    suppmin=255
    symbol reedmin=50
    
    
    
    do
    	gosub Bat
    	high c.0	'green led on
    	high Tx
    	low con	'put into command mode (to communicate at previouslt set baud rate)
    	pause 160	'wait 40 msecs for module to go into command mode
    
    	input con	'take out of command mode and tri-state c.1
    	pause 160	'wait 40 msecs for module to go into pass through mode
    
    	low c.0	'green led off
    
    	inc WaterCnt	'increment the water meter pulse counter
    
    	calibadc10 suppvol
    	suppvol=64*1023/suppvol*200/125	'Supply Voltage
    	suppvol=suppvol-200
    	suppmax=suppvol min suppmax
    	suppmin=suppvol max suppmin
    
    
    	serout tx,T9600_16,(#WaterCnt," - ",#suppvol,",",#suppmax,",",#suppmin,",",#WaterCnt,cr,lf)
    	pause 150	'it just seems to need a pause here of at least 50 for it to work
    
    
    	if BatOvrVolt=0 then: gosub sleepmod:endif	'put HC-12 to sleep to save power if battery not overcharged
    loop
    
    
    
    Bat:
    do
      	pullup %00010000
     	readadc c.4,b0
     	pullup %00000000
    	BatVoltInt=BatVoltInt+1 and $0FFF	'should overflow about every 5 minutes
    	if BatVoltInt=0 then
    		calibadc10 suppvol
    		suppvol=64*1023/suppvol*200/125	'Supply Voltage
    		suppvol=suppvol-200
    		if suppvol>BattHigh then
    			if BatOvrVolt=0 then
    				BatOvrVolt=1
    				low con		'put into command mode (to communicate at previouslt set baud rate)
    				pause 160	'wait 40 msecs for module to go into command mode
    				input con	'take out of command mode and tri-state c.1
    				pause 160	'wait 40 msecs for module to go into pass through mode
    			endif
    		endif
    	
    		if suppvol<BattLow then
    			if BatOvrVolt>0 then
    				BatOvrVolt=0
    				call sleepmod
    			endif
    		endif
    	
    	else
    		nap 2		'nap for 144 msecs if contacts still open
          endif
    
    loop until b0<reedmin
    RETURN
    
    '-----------------------------------------------------------------------------------
    sleepmod:	'Puts module to sleep - takes about 150 msecs and leaves it in pass through mode
    temp=5
    
    high Tx
    low con	'put into command mode (to communicate at previouslt set baud rate)
    pause 160	'wait 40 msecs for module to go into command mode
    
    serout tx,T9600_16,("AT+SLEEP")  
    bptr=28
    serin [150],rx,T9600_16,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc,@bptrinc
    
    b0=bptr-1
    pause 160	'wait 40 msecs to action sleep command before going back to pass through mode
    input con	'take out of command mode by tri-stating c.1
    input tx  	'tri-state c.2 while asleep
    
    RETURN
    Last edited by BESQUEUT; 13-02-2018 at 18:37.
    There are 10 types of people in the world: those who understand binary, and those who don't.

  10. #10
    Member
    Join Date
    Sep 2007
    Location
    Canberra, Australia
    Posts
    90

    Default

    Thanks Besqueut for your alternative code. I don’t think it is equivalent and it needs an inverse version of your Bat subroutine to wait until the reed switch opens. However I take yours and Hippy’s point that structured code would be easier for everyone (including me) to understand. My excuse is that old habits die hard and this program started life as a quick and dirty replacement of a wired connection that had become buried in foliage and just about impossible to maintain. I hoped that I could re-use some existing hardware I had and the program evolved to something more complex when I added battery voltage checking and realized that that needed to be done independently of flow through the meter. The battery checking would ideally be done as an independent second task but in this case I needed the higher operating speed and I also wasn’t too sure how the timing of this second task would go with naps (instead of pauses) in the main program.

    While I agree that my code isn’t pretty, I do think it’s logical and should be capable of being compiled without causing periodic restarts. I managed to get the code working – principally by changing a single “nap 3” command into two consecutive “nap 2” commands - and its currently meeting my requirements of maintaining a real time, in-house record of our water consumption. At some point, I will look at improving this communication link which, in addition to better structured code, should also involve sending binary rather than ASCII data, a slower transmission speed with more error checking and less HC-12 transmission power.

    The reason that I started this thread was to advise others of the possibility that there was a bug with the use of the nap command in PE5. As I stated earlier, I have no immediate plans to install PE6 as, until now at least, PE5 has worked quite satisfactorily for my simple needs and at my age the novelty of learning (and unlearning) new operating systems has well and truly passed. I'm an engineer and really just want to use computers to solve my problems and I need some convincing that a new system really has sufficient advantages for me personally before I buy into it.

    I spent some time to provide the forum with a simple version of my program which still failed for me and that needed minimal testing hardware in the hope that some kind soul could confirm that they also got continual program restarts under PE5 and then to try it under PE6 and tell me if that solved the problem. Mind you, even if a PE6 compile did solve the problem, I still wouldn’t be totally convinced that there was no problem as I think the “fix” I found under PE5 of using two consecutive “nap 2” commands instead of a single “nap 3” isn’t a logical method of solving the problem in PE5 either. The “fix” in the move to PE6 might similarly just be a fluke.

    Ideally, I’d like to know the reasons for this restarting problem in PE5 so that it can be confirmed that a move to PE6 is the only reliable alternative to overcome this problem.